Where did I fail to set up heated chamber om SKR 1.3 ?

Posted by Andke 
Where did I fail to set up heated chamber om SKR 1.3 ?
November 18, 2024 04:46AM
Marlin 2.1.1.1 build target LPC1768 pinmapping.h says: #define P2_04 0x44

I have this in configuration.adv:
#if TEMP_SENSOR_CHAMBER
#define TEMP_CHAMBER_PIN TEMP_1_PIN  //  #### Uses E1 thermistor input
  #define HEATER_CHAMBER_PIN      P2_04

The chamber temperature sensor works - the LCD allows me to set a target chamber temperature.
but the fan never starts.

There is no voltage on HE1 output marked 2.4 : [github.com]
The fuses are ok.

I have never used HE1 before, so there is no reason to believe that the FET is defective.


I have also this, just enabled, and default PIDs and limits.:
#define PIDTEMPCHAMBER
//#define CHAMBER_LIMIT_SWITCHING

/**
 * Max Chamber Power
 * Applies to all forms of chamber control (PID, bang-bang, and bang-bang with hysteresis).
 * When set to any value below 255, enables a form of PWM to the chamber heater that acts like a divider
 * so don't use it unless you are OK with PWM on your heater. (See the comment on enabling PIDTEMPCHAMBER)
 */
#define MAX_CHAMBER_POWER 255 // limits duty cycle to chamber heater; 255=full current

#if ENABLED(PIDTEMPCHAMBER)
  #define MIN_CHAMBER_POWER 0
  //#define PID_CHAMBER_DEBUG // Print Chamber PID debug data to the serial port.

  // Lasko "MyHeat Personal Heater" (200w) modified with a Fotek SSR-10DA to control only the heating element
  // and placed inside the small Creality printer enclosure tent.
  //
  #define DEFAULT_chamberKp 37.04
  #define DEFAULT_chamberKi 1.40
  #define DEFAULT_chamberKd 655.17
  // M309 P37.04 I1.04 D655.17

  // FIND YOUR OWN: "M303 E-2 C8 S50" to run autotune on the chamber at 50 degreesC for 8 cycles.
#endif // PIDTEMPCHAMBER

#if ANY(PIDTEMP, PIDTEMPBED, PIDTEMPCHAMBER)
  //#define PID_OPENLOOP          // Puts PID in open loop. M104/M140 sets the output power from 0 to PID_MAX
  //#define SLOW_PWM_HEATERS      // PWM with very low frequency (roughly 0.125Hz=8s) and minimum state time of approximately 1s useful for heaters driven by a relay
  #define PID_FUNCTIONAL_RANGE 10 // If the temperature difference between the target temperature and the actual temperature
                                  // is more than PID_FUNCTIONAL_RANGE then the PID will be shut off and the heater will be set to min/max.

  //#define PID_EDIT_MENU         // Add PID editing to the "Advanced Settings" menu. (~700 bytes of flash)
  //#define PID_AUTOTUNE_MENU     // Add PID auto-tuning to the "Advanced Settings" menu. (~250 bytes of flash)
#endif


Additional info: the LCD clearly displays the chamber temp and allows to set target chamber temperature, but the Octorprint, for some reason, does not show anything about chamber-temperature, maybe comething is half-way configured?

Edited 1 time(s). Last edit at 11/18/2024 04:49AM by Andke.
Re: Where did I fail to set up heated chamber om SKR 1.3 ?
November 18, 2024 08:47AM
You have 2 things using P2_04

by default FAN1_PIN is using P2_04 nd default chamber fan is going to use this fan
but you have set #define HEATER_CHAMBER_PIN P2_04 /// pin for the chamber heater
Re: Where did I fail to set up heated chamber om SKR 1.3 ?
November 18, 2024 03:20PM
Damn! - you are good! - Thank you very much. grinning smiley