PID Tuning
Revision as of 17:09, 8 July 2014 by DaveX (talk | contribs) (Modifying Marlin Autotune parameters)
PID tuning refers to a proportional-integral-derivative control algorithm used in some repraps for hot ends and heated beds.
PID needs to have a P, I and D value defined to control the nozzle temperature. If the temperature ramps up quickly and slows as it approaches the target temperature, or if it swings by a few degrees either side of the target temperature, then the values are incorrect.
To run PID Autotune in Marlin and other firmares, run the following gcode with the nozzle cold:
 M303 E0 S200 C8
This will heat the first nozzle (E0), and cycle around the target temperature 8 times (C8) at the given temperature (S200) and return values for P I and D. An example from http://www.soliwiki.com/PID_tuning is:
bias: 92 d: 92 min: 196.56 max: 203.75
Ku: 32.59 Tu: 54.92
Clasic PID
Kp: 19.56
Ki: 0.71
Kd: 134.26
PID Autotune finished ! Place the Kp, Ki and Kd constants in the configuration.h
For Marlin, these values indicate the counts of the soft-PWM power control (0 to PID_MAX) for each element of the control equation. The softPWM value regulates the duty cycle of the f=(FCPU/16/64/256/2) control signal for the associated heater. The proportional (P) constant Kp is in counts/C, representing the change in the softPWM output per each degree of error. The integral (I) constant Ki in counts/(C*s) represents the change per each unit of time-integrated error. The derivative (D) constant Kd in counts/(C/s) represents the change in output expected due to the current rate of change of the temperature. In the above example, the autotune routine has determined that to control for a temperature of 200C, the soft PWM should be biased to 92 + 19.56*error + 0.71 * (sum of errors*time) -134.26 * dError/dT. The 'sum of errors*time' value is limited to the range +/-PID_INTEGRAL_DRIVE_MAX as set in Configuration.h. Commercial PID controllers typically use time-based parameters, Ti=Kp/Ki and Td=Kd/Kp, to specify the integral and derivative parameters. In the example above: Ti=19.56/0.71=27.54s, meaning an adjustment to compensate for integrated error over about 28 seconds; Td=134.26/19.56=6.86s, meaning an adjustment to compensate for the projected temperature about 7 seconds in the future.
The Kp, Ki, and Kd values can be entered with:
 M301 P19.56 I0.71 D134.26
In the case of multiple extruders (E0, E1, E2) these PID values are shared between the extruders, although the extruders may be controlled separately. If the EEPROM is enabled, save with M500. If it is not enabled, save these settings in Configuration.h.
For the bed, use:
 Bed: M303 E-1 S60 C8
and save bed settings with:
 M304 P1 I2 D3
For manual adjustments:
  • if it overshoots a lot and oscillates, either the integral gain needs to be increased or all gains should be reduced
  • Too much overshoot? Increase D, decrease P.
  • Response too damped? Increase P.
  • Ramps up quickly to a value below target temperature (0-160 fast) and then slows down as it approaches target (160-170 slow, 170-180 really slow, etc) temperature? Try increasing the I constant.
See also Wikipedia's PID_controller and Zeigler-Nichols tuning method. Marlin autotuning (2014-01-20, https://github.com/ErikZalm/Marlin/blob/Marlin_v1/Marlin/temperature.cpp#L250 ) uses the Ziegler-Nichols 'Classic' method, which first finds a gain which maximizes the oscillations around the setpoint, and uses the amplitude and period of these oscillations to set the proportional, integral, and derivative terms.
The default Marlin M303 calculates a set of Ziegler-Nichols "Classic" parameters based on the Ku (Ultimate Gain) and the Pu (Ultimate Period), where the Ku and Pu are determined by searching for a biased BANG-BANG oscillation around an average power level that produces oscillations centered on the setpoint. (See https://github.com/ErikZalm/Marlin/blob/Marlin_v1/Marlin/temperature.cpp#L238 )
    Kp_classic=Ku*0.6
    Ki_classic=2*Kp_classic/Tu
    Kd_classic=Kp_classic*Tu/8
You can transform these "Classic" parameters into the Zeigler-Nichols "Some Overshoot" set with:
    Kp=Kp_classic*0.55
    Ki=Ki_classic/2
    Kd=Kd_classic*8/3
Or the Z-N "No Overshoot" set:
    Kp=Kp_classic/3
    Ki=Ki_classic
    Kd=Kd_classic*8/3
Note that the multipliers for the autotuning parameters each have only one significant digit (implying 10% maximum precision), and that the other schemes differ by factors of 2 or 3. PID autotuning and tuning isn't terribly precise, and changes in the parameters by factors of 5 to 50% are perfectly reasonable.
In Marlin, the parameters that control and limit the PID controller can have more significant effects than the popular PID parameters. For example, PID_MAX and PID_FUNCTIONAL_RANGE, and PID_INTEGRAL_DRIVE_MAX can each have dramatic, unexpected effects on PID behavior. For instance, a too-large PID_MAX on a high-power heater can make autotuning impossible; a too-small PID_FUNCTIONAL_RANGE can cause odd reset behavior; a too large PID_FUNCTIONAL_RANGE can guarantee overshoot; and a too-small PID_INTEGRAL_DRIVE_MAX can cause droop.
PID Tuning by Commercial PID
If you have access to a PID controller unit and a compatible thermal probe that fits down into your hotend, you can use them to tune your PID and calibrate your thermistor.
Connection of the output of the PID to your heater varies depending on your electronics. (I used a 1K2:4K7 voltage divider to drop the 22V output of the PID to 5V for my bread-boarded VNP4904)
After the PID is connected you can use it to measure the nozzle temperature and correlate it with the thermistor readings and resistances.
Conversion from the commercial PID values of kP in %fullscale, Ti in seconds, and Td in seconds is as follows:
       Kp_marlin = 255 * kP_%fs / 100             (counts/C)
       Ki_marlin = Kp_marlin/Ti                   (counts/(C*s))
       Kd_marlin = Td/Kp_marlin                   (counts/(C/s))
As an example, a $30 MYPIN TD4-SNR 1/16 DIN PID temperature controller and $10 type-K probe can hold a particular Wildseyed hotend with a 6.8ohm resistor at 185.0C+/-0.1C using 12V with about a 43.7% duty cycle, or 0.437*12*12/6.8=9.25W. Invoking the autotuning on the controller produces these parameters: P=0.8%/C, I=27s, D=6.7s. Converting these to Marlin PID values:
       Kp_marlin = 255counts/fs * 0.8% / (100%/fs) = 2.04 counts/C
       Ki_marlin = Kp_marlin/Ti = 2.04counts/C/(27s) = 0.7 counts/(C*s)
       Kd_marlin = Td/Kp_marlin = 6.7s/(2.04 counts/C) = 3.3 counts/(C/s)
Differences between the results can be caused by physical differences in the systems, (e.g: the thermocouple is closer to the heater than the thermistor,) or by different choices of autotuning parameters (e.g.: the MYPIN TD4 autotuning process is a proprietary black box, while Marlin uses Zeigler-Nichols "Classic" method.)
The Temperature/resistance table below was developed by using the PID+thermocouple system to set temperatures on a sample hotend by controlling the heater while measuring the thermistor resistance. These values can be used with Nophead's http://hydraraptor.blogspot.com/2012/11/more-accurate-thermistor-tables.html or Marlin's https://github.com/ErikZalm/Marlin/blob/Marlin_v1/Marlin/createTemperatureLookupMarlin.py to create calibrated thermistor tables. The PID column collects the autotuning values produced by the PID controller for the indicated temperature. The kP,Ki,Kd lists the converted parameters.
Temp DutyCycle Thermistor R Commercial PID Kp,Ki,Kd
60.0 6.0 31630
100.0 15.7 10108 1.1%/C, 35.5s, 8.8s 2.81, 0.08, 3.13
120.0 22.5 5802 1.0%/C, 32.0s, 8.0s 2.55, 0.08, 3.14
135.0 26.5 3967
150.0 28.5 2840 1.2%/C, 29.0s, 7.2s 3.06, 0.10, 2.35
170.0 34.0 1829
185.0 43.7 1347 0.8%/C, 27s, 6.7s 2.04, 0.08, 3.28
190.0 45.9 1200 0.8%/C, 26s, 6.5s 2.04, 0.08, 3.18
200.0 51.0 977